ChemProCal Academy ChemProCal Academy Academy
🔥 1d Streak
⚡ 0 XP
⚙ + Open Calculator Login Sign Up
Learn / Safety Relief & Control Valves / Pressure Relief Valve Sizing (API 520 & 526)
Pressure Relief Valve Sizing (API 520 & 526) 0 Practice Questions ⚡ Live Calculator Connected

Vapor / Gas Relief Sizing (Critical vs Subcritical Flow)

API RP 520 Part I sizing formulation for sonic (critical) and subsonic gas/vapor flow, ideal vs real gas correction factors, and temperature ratio effects.

⚡ Open Live Tool Practice Questions ↓

1. Theoretical Foundations & Engineering Mechanics

API RP 520 Vapor & Gas Sizing Equations

Gas flow through a converging nozzle reaches sonic velocity (choked flow) at the nozzle throat when upstream relieving pressure exceeds the critical flow pressure.

1. Critical Flow Criterion

Critical flow occurs when the ratio of downstream absolute backpressure $P_b$ to absolute upstream relieving pressure $P_1$ is less than or equal to the critical pressure ratio $\eta_{crit}$:
$$\frac{P_b}{P_1} \le \eta_{crit} = \left(\frac{2}{k+1}\right)^{\frac{k}{k-1}}$$
where $k = C_p/C_v$ is the ideal gas heat capacity ratio (isentropic expansion exponent).
For natural gas ($k \approx 1.25$), $\eta_{crit} \approx 0.55$.

2. Critical Flow Sizing Equation

Under critical conditions, flow rate depends solely on upstream stagnation conditions:
$$A = \frac{W}{C K_d P_1 K_b K_c} \sqrt{\frac{T Z}{M}}$$
where:
- $A$: Required effective discharge area ($\text{in}^2$ or $\text{mm}^2$)
- $W$: Relieving flow rate ($\text{lb/h}$ or $\text{kg/h}$)
- $C$: Gas expansion coefficient function of $k$:
$$C = 520 \sqrt{k \left(\frac{2}{k+1}\right)^{\frac{k+1}{k-1}}}$$
- $K_d$: Effective discharge coefficient ($0.975$ for API gas sizing)
- $P_1$: Relieving pressure ($P_{set} + \text{Overpressure} + P_{atm}$)
- $K_b$: Backpressure capacity derating factor ($1.0$ for critical flow or conventional PSVs)
- $K_c$: Rupture disc combination factor ($1.0$ without disc, $0.90$ with rupture disc installed upstream)
- $T$: Absolute relieving temperature ($\text{R}$ or $\text{K}$)
- $Z$: Gas compressibility factor at relieving conditions
- $M$: Gas molecular weight ($\text{kg/kmol}$ or $\text{lb/lbmol}$)

3. Subcritical Flow Formulation

When $P_b/P_1 > \eta_{crit}$, acoustic choking does not occur at the throat, requiring subcritical flow equation with factor $F_2$.

2. Governing Equations & Mathematical Formulation

$$C = 0.03948 \sqrt{k \left(\frac{2}{k+1}\right)^{\frac{k+1}{k-1}}} \quad \text{[SI Units]}$$

$$A = \frac{13160 \cdot W}{C K_d P_1 K_b K_c} \sqrt{\frac{T Z}{M}} \quad [A: \text{mm}^2, W: \text{kg/h}, P_1: \text{kPaa}]$$

$$A = \frac{W}{C K_d P_1 K_b K_c} \sqrt{\frac{T Z}{M}} \quad [A: \text{in}^2, W: \text{lb/h}, P_1: \text{psia}]$$

💡 Formulated according to international process engineering standards and dimensionless groups.
📌 Key Engineering Assumptions

• Isentropic nozzle expansion with ideal or near-ideal gas compressibility behavior.
• Relieving pressure $P_1 = P_{set} \times (1 + \%\text{overpressure}/100) + P_{atm}$.
• Single-phase pure gas or vapor mixture without entrained liquid mist or droplet condensation during expansion.

⚠️ Common Industrial Pitfalls

• Forgetting to convert gauge pressure to absolute pressure ($P_1 = P_{gauge} + 1.013\text{ bar}$) before calculating critical ratio and orifice area.
• Using standard conditions ($15^\circ\text{C}, 1\text{ atm}$) compressibility factor $Z$ instead of $Z$ at high relieving pressure and temperature.
• Applying critical equations when flare header backpressure is greater than 55% of relieving pressure in subcritical regimes.

3. Applied Engineering Worked Example

Design Problem Specification

Fluid: Methane / Ethane Natural Gas ($M = 19.5\text{ kg/kmol}$, $k = 1.28$)
Relieving Rate: $W = 35,000\text{ kg/h}$
Set Pressure: $P_{set} = 28.0\text{ barg}$
Allowable Overpressure: $10\% \implies P_{rel} = 30.8\text{ barg} = 31.813\text{ bara} = 3,181.3\text{ kPa (abs)}$
Relieving Temperature: $T = 65^\circ\text{C} = 338.15\text{ K}$, $Z = 0.88$
Installation: Conventional PSV with atmospheric tailpipe ($P_b = 1.013\text{ bara}$), no rupture disc ($K_c = 1.0$)

Step-by-Step Mathematical Derivation & Verification
  1. Check Critical Flow Ratio:
    $$\eta_{crit} = \left(\frac{2}{1.28 + 1}\right)^{\frac{1.28}{1.28 - 1}} = (0.8772)^{4.571} = 0.549$$
    $$\frac{P_b}{P_1} = \frac{1.013}{31.813} = 0.0318 \ll 0.549 \implies \text{Critical Choked Flow confirmed. } K_b = 1.0$$

  2. Calculate Gas Expansion Coefficient $C$:
    $$C = 0.03948 \sqrt{1.28 \left(\frac{2}{2.28}\right)^{\frac{2.28}{0.28}}} = 0.03948 \sqrt{1.28 \times 0.3444} = 0.03948 \times 0.6639 = 0.02621$$

  3. Calculate Required Area (SI Form):
    $$A = \frac{13160 \times 35,000}{0.02621 \times 0.975 \times 3,181.3 \times 1.0 \times 1.0} \sqrt{\frac{338.15 \times 0.88}{19.5}}$$
    $$A = \frac{460,600,000}{81,296.8} \times \sqrt{15.26} = 5,665.7 \times 3.9064 = 2,213.3\text{ mm}^2$$
    In US customary units: $A = 2,213.3 / 645.16 = 3.431\text{ in}^2$

  4. Select API 526 Standard Orifice:
    - L Orifice ($2.853\text{ in}^2$) < $3.431\text{ in}^2$
    - M Orifice ($3.600\text{ in}^2$) > $3.431\text{ in}^2$
    Selected: Orifice M ($A = 3.600\text{ in}^2 = 2323\text{ mm}^2$), typically a 4M6 valve.

Interactive Practice Drill: Vapor / Gas Relief Sizing (Critical vs Subcritical Flow)

Instant answer checking, step rationales, and tolerance scoring.
Question 1 of 15
Loading interactive questions...

Completed this lesson?

Record your study progress, build your daily streak, and unlock +25 XP toward your next engineering tier.

⚡

Connected ChemProCal Tool

Run numerical simulations with real physical property packages.
Gas Choke & Pressure Relief / Depressurization Analyzer

Analyze compressible gas flow across wellhead chokes (bean sizes 1/64" to 64/64") and flare relief orifices. …

Verified Equations Engineering Tolerances
Launch Live Tool ⚡