Two-Phase Flashing & Non-Flashing Relief Sizing (API 520 Omega / HEM)
API RP 520 Annex C Two-Phase flashing and non-flashing relief sizing utilizing the Omega parameter (omega method) and Homogeneous Equilibrium Model (HEM).
1. Theoretical Foundations & Engineering Mechanics
Two-Phase Flashing Relief & The Omega ($\omega$) Method
When saturated or subcooled liquids enter a relief valve nozzle, depressurization below the bubble point triggers violent vaporization (flashing). The dramatic expansion of vapor drastically limits mass flux, causing conventional single-phase liquid or vapor equations to underestimate required orifice area by up to 300% to 500%.
1. The Omega ($\omega$) Parameter
Developed by Dr. J. C. Leung and DIERS, the dimensionless Omega parameter characterizes the fluid compressibility (rate of flashing):
- For flashing liquids (near saturation):
$$\omega = 9 \left(\frac{\rho_{l1}}{\rho_{9}} - 1\right)$$
where $\rho_{l1}$ is inlet liquid density and $\rho_9$ is two-phase mixture density at 90% of absolute inlet relieving pressure ($0.9 P_1$).
- For two-phase inlet gas/liquid mixtures:
$$\omega = x_1 \omega_g + (1 - x_1) \omega_l$$
2. Critical Pressure Ratio for Two-Phase Flow
The critical pressure ratio $\eta_c = P_c / P_1$ is computed from $\omega$:
$$\eta_c = \left(\frac{2}{\omega + 1}\right)^{\frac{\omega}{\omega - 1}}$$
For high flashing fluids ($\omega \approx 10$ to $30$), critical pressure ratio $\eta_c$ ranges from $0.75$ down to $0.55$.
3. Mass Flux Sizing Equation
The critical mass flux $G_c$ at the nozzle throat is:
$$G_c = \eta_c \sqrt{\frac{P_1 \rho_{l1}}{\omega}}$$
The required effective discharge area is:
$$A = \frac{W}{K_d G_c K_b}$$
where $K_d = 0.85$ is the recommended certified discharge coefficient for two-phase nozzle service.
2. Governing Equations & Mathematical Formulation
$$\omega = 9 \left(\frac{v_9 - v_{l1}}{v_{l1}}\right) = 9 \left(\frac{\rho_{l1}}{\rho_9} - 1\right)$$
$$\eta_c \left[ \omega \ln\left(\frac{1}{\eta_c}\right) - (\omega - 1)(1 - \eta_c) \right] = \frac{1}{2}$$
$$G_c = \eta_c \sqrt{\frac{2 P_1 \rho_{l1} \left[ \omega \ln(1/\eta_c) - (\omega - 1)(1 - \eta_c) \right]}{\left[ \omega (1/\eta_c - 1) + 1 \right]^2}}$$
$$A = \frac{W}{K_d G_c}$$
• Homogeneous Equilibrium Model (HEM): vapor and liquid travel at equal velocity (zero slip) and maintain thermodynamic phase equilibrium throughout the nozzle.
• Frozen flow assumption applies only to extremely short orifices (L/D < 0.1) or non-flashing gas-liquid bubbly mixtures.
• Density at 90% pressure is evaluated via isentropic flash in process simulator.
• Treating flashing water/condensate or LPG as pure liquid, which leads to catastrophic undersizing.
• Sizing flashing relief using separate liquid and vapor areas added together (the separate stream method), which severely underestimates required throat area.
• Ignoring massive reaction forces generated by two-phase momentum expansion in tailpipes.
3. Applied Engineering Worked Example
Fluid: Saturated Liquid Butane Relieving during Fire
Relieving Rate: $W = 45,000\text{ kg/h}$ ($12.5\text{ kg/s}$)
Relieving Pressure ($P_1$): $12.0\text{ bara} = 1.20 \times 10^6\text{ Pa}$
Inlet Liquid Density: $\rho_{l1} = 540\text{ kg/m}^3$
Mixture Density at $0.9 P_1$ ($10.8\text{ bara}$): $\rho_9 = 180\text{ kg/m}^3$
Discharge Coefficient: $K_d = 0.85$
-
Compute Leung Omega Parameter ($\omega$):
$$\omega = 9 \times \left(\frac{540}{180} - 1\right) = 9 \times (3.0 - 1) = 9 \times 2.0 = 18.0$$ -
Determine Critical Pressure Ratio ($\eta_c$):
For $\omega = 18.0$, API 520 Annex C chart / approximation yields:
$$\eta_c \approx 0.58$$ -
Calculate Critical Mass Flux ($G_c$):
$$G_c \approx \eta_c \sqrt{\frac{P_1 \rho_{l1}}{\omega}} = 0.58 \times \sqrt{\frac{1,200,000 \times 540}{18}} = 0.58 \times \sqrt{36,000,000} = 0.58 \times 6,000 = 3,480\text{ kg/(m}^2\cdot\text{s)}$$ -
Calculate Required Orifice Area:
$$A = \frac{12.5\text{ kg/s}}{0.85 \times 3,480\text{ kg/(m}^2\cdot\text{s)}} = \frac{12.5}{2,958} = 0.004226\text{ m}^2 = 4,226\text{ mm}^2$$
$$A = 4,226 / 645.16 = 6.55\text{ in}^2$$ -
Select API Orifice:
- P Orifice ($6.38\text{ in}^2$) < $6.55\text{ in}^2$
- Q Orifice ($11.05\text{ in}^2$) > $6.55\text{ in}^2$
Selected: Q Orifice (6Q8 valve Body).