Vapor-Compression Refrigeration Cycles & Refrigerants
Standard vapor-compression refrigeration cycle, pressure-enthalpy (P-h) diagrams, compressor displacement, evaporator duty, condenser heat rejection, and COP.
1. Theoretical Foundations & Engineering Mechanics
Vapor-Compression Refrigeration Cycles
The vapor-compression refrigeration cycle provides chilled cooling for process plant condensation, NGL recovery, HVAC, and food preservation.
1. The Four Cycle Stages
- Isentropic Compression ($1 \rightarrow 2$): Low-pressure saturated refrigerant vapor from the evaporator is compressed to high condensing pressure by a compressor: $w_{comp} = h_2 - h_1$.
- Isobaric Heat Rejection ($2 \rightarrow 3$): Superheated gas de-superheats and condenses to saturated liquid in an air or water-cooled condenser: $q_{cond} = h_2 - h_3$.
- Isenthalpic Throttling ($3 \rightarrow 4$): Saturated high-pressure liquid expands across an expansion valve (TXV) into a cold low-pressure two-phase mixture: $h_4 = h_3$.
- Isobaric Heat Absorption ($4 \rightarrow 1$): Cold refrigerant boils inside the evaporator, absorbing thermal energy from the process fluid: $q_{evap} = h_1 - h_4$.
2. Coefficient of Performance (COP)
The efficiency of a refrigeration cycle is measured by its Coefficient of Performance:
$$COP = \frac{\text{Refrigeration Effect}}{\text{Work Input}} = \frac{q_{evap}}{w_{comp}} = \frac{h_1 - h_4}{h_2 - h_1}$$
Commercial industrial refrigeration systems typically operate with $COP = 2.5$ to $4.5$.
2. Governing Equations & Mathematical Formulation
$$\dot{Q}_{evap} = \dot{m}_{ref} (h_1 - h_4)$$
$$\dot{W}_{comp} = \frac{\dot{m}_{ref} (h_{2s} - h_1)}{\eta_{is}}$$
$$\dot{Q}_{cond} = \dot{m}_{ref} (h_2 - h_3) = \dot{Q}_{evap} + \dot{W}_{comp}$$
$$COP = \frac{\dot{Q}_{evap}}{\dot{W}_{comp}} = \frac{h_1 - h_4}{h_2 - h_1} < COP_{Carnot} = \frac{T_C}{T_H - T_C}$$
$$1\text{ Ton of Refrigeration (TR)} = 12,000\text{ Btu/h} = 3.517\text{ kW}$$
• Negligible pressure drops in interconnecting refrigerant piping.
• Refrigerant leaves evaporator as dry saturated vapor ($x = 1.0$) or with $5^\circ\text{C}$ superheat.
• Refrigerant leaves condenser as saturated liquid ($x = 0$) or with $3^\circ\text{C}$ subcooling.
• Allowing liquid droplets to enter compressor suction (liquid slugging destroys compressor valves and pistons).
• Using high condensing temperatures due to fouled condenser tubes, which spikes compressor power and slashes COP.
• Neglecting oil return: lubricating oil carried into evaporators coats heat transfer surfaces and impairs duty.
3. Applied Engineering Worked Example
Refrigerant: Propane (R290) Chiller System
Duty: $\dot{Q}_{evap} = 500\text{ kW}$ ($142.2\text{ TR}$) at $T_{evap} = -20^\circ\text{C}$ ($P_1 = 2.45\text{ bar}$)
Condenser: Water-cooled at $T_{cond} = 40^\circ\text{C}$ ($P_2 = 13.7\text{ bar}$)
Enthalpy Points:
- Evaporator Outlet (Saturated Vapor): $h_1 = 562.0\text{ kJ/kg}$, $s_1 = 2.428\text{ kJ/(kg}\cdot\text{K)}$
- Isentropic Discharge: $h_{2s} = 638.0\text{ kJ/kg}$
- Condenser Outlet (Saturated Liquid): $h_3 = 265.0\text{ kJ/kg} = h_4$
Compressor Efficiency: $\eta_{is} = 0.80$
-
Compute Required Refrigerant Mass Flow Rate:
$$q_{evap} = h_1 - h_4 = 562.0 - 265.0 = 297.0\text{ kJ/kg}$$
$$\dot{m}_{ref} = \frac{\dot{Q}_{evap}}{q_{evap}} = \frac{500\text{ kW}}{297.0\text{ kJ/kg}} = \mathbf{1.6835\text{ kg/s}}$$ -
Compute Actual Compressor Power Required:
$$w_{is} = h_{2s} - h_1 = 638.0 - 562.0 = 76.0\text{ kJ/kg}$$
$$w_{act} = \frac{76.0}{0.80} = 95.0\text{ kJ/kg}$$
$$\dot{W}_{comp} = 1.6835\text{ kg/s} \times 95.0\text{ kJ/kg} = \mathbf{159.9\text{ kW}}$$ -
Compute System COP:
$$COP = \frac{\dot{Q}_{evap}}{\dot{W}_{comp}} = \frac{500\text{ kW}}{159.9\text{ kW}} = \mathbf{3.127}$$ -
Compute Condenser Heat Rejection:
$$\dot{Q}_{cond} = 500 + 159.9 = \mathbf{659.9\text{ kW}}$$