Absorption Refrigeration Systems (LiBr-Water & Ammonia-Water)
Absorption refrigeration cycles (LiBr-Water and Ammonia-Water), thermal COP, generator heat input, absorber mechanics, and waste heat recovery.
1. Theoretical Foundations & Engineering Mechanics
Absorption Refrigeration Cycles ($LiBr$-$H_2O$ & $NH_3$-$H_2O$)
Absorption refrigeration systems replace the power-hungry mechanical compressor with a thermally driven liquid pump-absorber-generator loop, utilizing low-grade waste heat (steam, hot flue gas, or jacket water) to provide industrial chilling.
1. Fundamental Principle of Thermally Driven Cooling
Pumping an incompressible liquid from low to high pressure consumes less than $1\%$ of the work required to compress a vapor ($w = \int v dP$, and $v_{liquid} \ll v_{vapor}$):
1. Evaporator: Refrigerant boils at low pressure, producing cooling.
2. Absorber: Low-pressure vapor is absorbed into a liquid absorbent solution, releasing heat of solution to cooling water.
3. Solution Pump: A small liquid pump pushes rich solution to high pressure.
4. Generator (Desorber): Waste heat ($80$ to $160^\circ\text{C}$) boils the refrigerant out of solution at high pressure.
5. Condenser: Refrigerant vapor condenses to liquid, ready for expansion.
2. Working Pairs
- Lithium Bromide - Water ($LiBr$-$H_2O$): Water is the refrigerant; $LiBr$ salt is the absorbent. Non-toxic, high thermal efficiency ($COP_{th} \approx 0.7$ for single-effect, $1.2$ for double-effect). Limited to chilling temperatures above $0^\circ\text{C}$ ($4 - 7^\circ\text{C}$ for HVAC air conditioning) because water freezes.
- Ammonia - Water ($NH_3$-$H_2O$): Ammonia is the refrigerant; water is the absorbent. Capable of sub-zero cryogenic cooling down to $-30^\circ\text{C}$ to $-50^\circ\text{C}$ for process freezing. Requires a rectification column to strip water vapor out of ammonia.
2. Governing Equations & Mathematical Formulation
$$COP_{thermal} = \frac{\dot{Q}_{evap}}{\dot{Q}_{generator} + \dot{W}_{pump}} \approx \frac{\dot{Q}_{evap}}{\dot{Q}_{gen}}$$
$$COP_{max,Carnot} = \left( \frac{T_{evap}}{T_{cond} - T_{evap}} \right) \left( \frac{T_{gen} - T_{abs}}{T_{gen}} \right)$$
$$\dot{Q}_{rejected} = \dot{Q}_{absorber} + \dot{Q}_{condenser} = \dot{Q}_{evap} + \dot{Q}_{gen}$$
• Pumping mechanical work is negligible relative to thermal generator heat duty.
• Rich solution heat exchanger (SHE) pre-heats rich solution entering generator, boosting COP.
• Cooling water available at $25 - 30^\circ\text{C}$ to reject combined condenser and absorber heat.
• Operating LiBr systems with high generator temperatures and cold condenser temperatures, causing $LiBr$ crystallization that solidifies the solution piping.
• Sizing cooling towers assuming absorption units have the same heat rejection as electric chillers; absorption chillers reject almost double the heat of electric chillers ($\dot{Q}_{abs} + \dot{Q}_{cond}$).
• Air leaks into vacuum $LiBr$ chillers ($P_{evap} \approx 6\text{ mmHg}$), destroying performance.
3. Applied Engineering Worked Example
Waste Heat Source: Chemical Plant Refinery Flue Gas providing $\dot{Q}_{gen} = 3.0\text{ MW}$ heat at $140^\circ\text{C}$
Chiller Type: Single-Effect Ammonia-Water Absorption Chiller
Evaporation Temperature: $T_{evap} = -10^\circ\text{C}$ ($263.15\text{ K}$)
Thermal COP: Measured $COP_{th} = 0.58$
-
Compute Refrigeration Cooling Capacity:
$$\dot{Q}_{evap} = COP_{th} \times \dot{Q}_{gen} = 0.58 \times 3.0\text{ MW} = \mathbf{1.74\text{ MW}} = 494.7\text{ TR}$$ -
Calculate Total Heat Rejection to Cooling Tower:
$$\dot{Q}_{rejected} = \dot{Q}_{gen} + \dot{Q}_{evap} = 3.0\text{ MW} + 1.74\text{ MW} = \mathbf{4.74\text{ MW}}$$ -
Cooling Water Flow Rate Required ($\Delta T_{cw} = 8^\circ\text{C}$):
$$\dot{m}_{cw} = \frac{4,740\text{ kW}}{4.184\text{ kJ/(kg}\cdot\text{K)} \times 8.0\text{ K}} = \frac{4,740}{33.472} = 141.6\text{ kg/s} = \mathbf{510\text{ m}^3/\text{h}}$$