Psychrometry, Humidification & Convective Drying

Psychrometric principles, air-water humidification and cooling, wet-bulb vs dry-bulb temperatures, adiabatic saturation, and cooling tower sizing.

⚡ Open Live Tool Practice Questions ↓

1. Theoretical Foundations & Engineering Mechanics

Psychrometry, Humidification & Convective Drying

Psychrometry deals with the thermodynamic and transport properties of gas-vapor mixtures, most notably moist air (water vapor in air).

1. Key Psychrometric Parameters

  • Humidity (Moisture Content $\boldsymbol{Y}$ or $\boldsymbol{\omega}$): Mass of water vapor per unit mass of dry air:
    $$Y = \frac{M_w p_w}{M_{air} (P - p_w)} = 0.622 \frac{p_w}{P - p_w}$$
  • Relative Humidity ($\boldsymbol{\phi}$ or $\boldsymbol{RH}$):
    $$RH = \frac{p_w}{P_w^{sat}(T)} \times 100\%$$
  • Wet-Bulb Temperature ($T_{wb}$): The steady-state equilibrium temperature attained by a wetted thermometer bulb exposed to a high-velocity air stream:
    $$h (T_{db} - T_{wb}) = k_y \lambda_w (Y_{wb}^* - Y)$$
    For the air-water system, the Lewis relation happens to equal unity ($Le = h / (k_y C_{pm}) \approx 1.0$), meaning the wet-bulb temperature equals the adiabatic saturation temperature ($T_{wb} \approx T_{as}$).

2. Cooling Tower Merkel Equation

In industrial wet cooling towers, water cools primarily via evaporative mass transfer into rising ambient air. The heat and mass transfer is integrated via the Merkel equation:
$$\frac{K a V}{L} = \int_{T_{w2}}^{T_{w1}} \frac{C_{pL} dT_w}{h_{air}^*(T_w) - h_{air}}$$
where $h_{air}^*$ is saturated air enthalpy at water temperature $T_w$ and $h_{air}$ is bulk air enthalpy.

2. Governing Equations & Mathematical Formulation

$$Y = 0.622 \frac{p_w}{P - p_w} \quad [\text{Humidity, kg water / kg dry air}]$$

$$RH = \frac{p_w}{P_w^{sat}(T_{db})} \times 100\%$$

$$h_{air} = C_{pa} T_{db} + Y (\Delta H_{vap0} + C_{pv} T_{db}) = 1.006 T + Y (2501 + 1.86 T)$$

$$\frac{K a V}{L} = \int_{T_{w,cold}}^{T_{w,hot}} \frac{C_{pL} dT}{h^*(T) - h} \quad [\text{Merkel Equation}]$$

💡 Formulated according to international process engineering standards and dimensionless groups.
📌 Key Engineering Assumptions

• Ideal gas mixture behavior for moist air at atmospheric pressure.
• Lewis relation $Le = 1.0$ valid for air-water systems.
• Merkel assumptions (water loss by evaporation is negligible in the mass balance, Lewis factor unity).
• Steady-state counter-current flow in cooling tower packing.

⚠️ Common Industrial Pitfalls

• Confusing relative humidity $RH = p_w / P_w^{sat}$ with percentage humidity $Y / Y_{sat}$.
• Assuming a cooling tower can cool water below the ambient wet-bulb temperature; $T_{wb}$ is the absolute thermodynamic limit (approach $= T_{cold} - T_{wb} > 3 - 5^\circ\text{C}$).
• Using dry-bulb temperature to size cooling towers; cooling towers are governed strictly by ambient wet-bulb temperature.
• Ignoring drift and blowdown losses; without regular blowdown, evaporative concentration causes severe mineral scaling.

3. Applied Engineering Worked Example

Design Problem Specification

Standard industrial operating and sizing conditions.

Step-by-Step Mathematical Derivation & Verification

Problem Statement:
Ambient air at $1.013\text{ bar}$ has dry-bulb temperature $T_{db} = 32^\circ\text{C}$ and relative humidity $RH = 60\%$. Given saturation vapor pressure of water at $32^\circ\text{C}$ is $P_w^{sat} = 4.757\text{ kPa}$ ($0.04757\text{ bar}$):
1. Calculate the partial pressure of water vapor $p_w$.
2. Calculate the humidity $Y$ in $\text{kg water / kg dry air}$.
3. Calculate the enthalpy of the moist air mixture $h_{air}$ in $\text{kJ/kg dry air}$.

Step-by-step Solution:
1. Calculate water vapor partial pressure $p_w$:
$$p_w = RH \times P_w^{sat} = 0.60 \times 4.757\text{ kPa} = \mathbf{2.8542\text{ kPa}} = 0.028542\text{ bar}$$

  1. Calculate humidity $Y$:
    $$Y = 0.622 \times \frac{p_w}{P - p_w} = 0.622 \times \frac{2.8542\text{ kPa}}{101.325 - 2.8542\text{ kPa}} = 0.622 \times \frac{2.8542}{98.471} = \mathbf{0.01803\text{ kg/kg dry air}}$$
    ($18.03\text{ g water / kg dry air}$).

  2. Calculate moist air enthalpy $h_{air}$:
    $$h_{air} = 1.006 T_{db} + Y (2501 + 1.86 T_{db})$$
    $$1.006 \times 32 = 32.192\text{ kJ/kg}$$
    $$2501 + (1.86 \times 32) = 2501 + 59.52 = 2560.52\text{ kJ/kg}$$
    $$Y \times 2560.52 = 0.01803 \times 2560.52 = 46.166\text{ kJ/kg}$$
    $$h_{air} = 32.192 + 46.166 = \mathbf{78.36\text{ kJ/kg dry air}}$$

Interactive Practice Drill: Psychrometry, Humidification & Convective Drying

Instant answer checking, step rationales, and tolerance scoring.
Question 1 of 8
Loading interactive questions...

Completed this lesson?

Record your study progress, build your daily streak, and unlock +25 XP toward your next engineering tier.

⚡

Connected ChemProCal Tool

Run numerical simulations with real physical property packages.
Psychrometric & HVAC Analyzer

Rigorous CoolProp inverse solver and HVAC process analysis for cooling, heating, and dehumidification loads.

Verified Equations Engineering Tolerances
Launch Live Tool ⚡