ChemProCal Academy ChemProCal Academy Academy
🔥 1d Streak
⚡ 0 XP
⚙ + Open Calculator Login Sign Up
Learn / Material & Energy Balances / Process Fundamentals & Degrees of Freedom
Process Fundamentals & Degrees of Freedom 15 Practice Questions ⚡ Live Calculator Connected

Psychrometric Charts, Relative Humidity & Dew Point Calculations

Examines humid air thermodynamics, absolute humidity, relative humidity, dry-bulb vs wet-bulb temperatures, dew point calculations, and psychrometric chart applications in process drying.

⚡ Open Live Tool Practice Questions ↓

1. Theoretical Foundations & Engineering Mechanics

Air-Water Vapor Thermodynamics

Humid air is modeled as a binary mixture of dry air (species $A$, $M_A = 28.964\text{ g/mol}$) and water vapor (species $B$, $M_B = 18.015\text{ g/mol}$) under total atmospheric pressure $P$:

$$P = p_A + p_w$$

Where $p_w$ is the partial pressure of water vapor.

Moisture Content Metrics

  1. Relative Humidity ($\phi$ or $RH$): The ratio of the actual water vapor partial pressure to the saturation vapor pressure $p_{sat}(T)$ at dry-bulb temperature $T$:
    $$RH = \phi = \frac{p_w}{p_{sat}(T)} \times 100\%$$
  2. Absolute Humidity / Humidity Ratio ($H$ or $Y$): The mass of water vapor per unit mass of bone-dry air:
    $$H = \frac{m_w}{m_{dry\_air}} = \frac{M_w p_w}{M_{air} (P - p_w)} = 0.622 \frac{p_w}{P - p_w}\text{ }\left[\frac{\text{kg H}_2\text{O}}{\text{kg Dry Air}}\right]$$
  3. Dew Point Temperature ($T_{dp}$): The temperature to which moist air must be cooled at constant pressure to reach saturation ($p_{sat}(T_{dp}) = p_w$). When $T = T_{dp}$, condensation commences.
  4. Wet-Bulb Temperature ($T_{wb}$): The steady-state non-equilibrium temperature reached by a wet thermometer wick exposed to rapid air circulation, where evaporative cooling balances convective heat gain:
    $$h (T_{db} - T_{wb}) = k_y \Delta H_{vap} (H_{sat,wb} - H)$$
    For air-water systems at ambient conditions, the Lewis number $Le = Sc / Pr \approx 1.0$, rendering the wet-bulb temperature virtually identical to the thermodynamic adiabatic saturation temperature.

2. Governing Equations & Mathematical Formulation

$$H = 0.622 \frac{p_w}{P - p_w}$$
$$RH = \frac{p_w}{p_{sat}(T_{db})} \times 100\%$$
$$p_w = p_{sat}(T_{dp})$$
$$h_m = C_{p,dry} T + H (\Delta H_{vap,0} + C_{p,vap} T)$$

💡 Formulated according to international process engineering standards and dimensionless groups.
📌 Key Engineering Assumptions

• Dry air and water vapor behave as ideal gases at atmospheric pressure.
• Total barometric pressure is constant at standard $101.325\text{ kPa}$ (1 atm).
• Lewis analogy holds for air-water mixtures ($Le \approx 1.0$).
• Liquid water condensing at dew point is pure and free of dissolved gases.

⚠️ Common Industrial Pitfalls

• Expressing absolute humidity per unit mass of total moist air instead of dry air ($kg_{H2O} / kg_{dry\_air}$).
• Assuming relative humidity remains constant when air is heated (heating air increases $p_{sat}(T)$, causing $RH$ to drop precipitously).
• Confusing wet-bulb temperature with dew-point temperature ($T_{db} \ge T_{wb} \ge T_{dp}$; they are equal only at $100\% RH$).
• Omitting atmospheric pressure corrections when using sea-level psychrometric charts at high elevations.

3. Applied Engineering Worked Example

Design Problem Specification

Air in a chemical plant compressor room is at dry-bulb temperature $T_{db} = 30.0^\circ\text{C}$ and relative humidity $RH = 60.0\%$ under standard barometric pressure $P = 101.325\text{ kPa}$.
The saturation vapor pressure of water at $30^\circ\text{C}$ is $p_{sat}(30^\circ\text{C}) = 4.246\text{ kPa}$.

  1. Calculate the partial pressure of water vapor $p_w$ in kPa.
  2. Compute the absolute humidity $H$ in $\text{kg H}_2\text{O}/\text{kg Dry Air}$.
  3. If the air is cooled to find its dew point, and the saturation pressure follows the Antoine equation:
    $$\ln(p_{sat}\text{ [kPa]}) = 16.3872 - \frac{3885.70}{T\text{ [}^\circ\text{C]} + 230.170}$$
    Calculate the dew point temperature $T_{dp}$.
  4. If $1000\text{ kg/h}$ of dry air passes through a chiller where it is cooled to $10.0^\circ\text{C}$ ($p_{sat}(10^\circ\text{C}) = 1.228\text{ kPa}$), calculate the rate of water condensed [kg/h].
Step-by-Step Mathematical Derivation & Verification

Step-by-Step Analytical Solution:

  1. Partial pressure of water vapor:
    $$p_w = (RH)(p_{sat}) = (0.600)(4.246\text{ kPa}) = \mathbf{2.5476\text{ kPa}}$$

  2. Absolute humidity $H$:
    $$H = 0.622 \frac{p_w}{P - p_w} = 0.622 \frac{2.5476}{101.325 - 2.5476} = 0.622 \frac{2.5476}{98.7774} = \mathbf{0.01604\text{ kg H}_2\text{O/kg Dry Air}}$$

  3. Dew point temperature $T_{dp}$:
    At dew point, $p_{sat}(T_{dp}) = p_w = 2.5476\text{ kPa}$.
    $$\ln(2.5476) = 0.93515$$
    $$0.93515 = 16.3872 - \frac{3885.70}{T_{dp} + 230.170}$$
    $$\frac{3885.70}{T_{dp} + 230.170} = 16.3872 - 0.93515 = 15.45205$$
    $$T_{dp} + 230.170 = \frac{3885.70}{15.45205} = 251.468$$
    $$T_{dp} = 251.468 - 230.170 = \mathbf{21.30^\circ\text{C}}$$

  4. Water condensation rate:
    At $10.0^\circ\text{C}$, the air is saturated ($RH = 100\%$):
    $$H_{out} = 0.622 \frac{1.228}{101.325 - 1.228} = 0.622 \frac{1.228}{100.097} = 0.00763\text{ kg/kg}$$
    Moisture removed per kg dry air: $\Delta H = 0.01604 - 0.00763 = 0.00841\text{ kg/kg}$
    $$\dot{m}_{condensed} = (1000\text{ kg dry air/h})(0.00841\text{ kg/kg}) = \mathbf{8.41\text{ kg/h}}$$

Interactive Practice Drill: Psychrometric Charts, Relative Humidity & Dew Point Calculations

Instant answer checking, step rationales, and tolerance scoring.
Question 1 of 15
Loading interactive questions...

Completed this lesson?

Record your study progress, build your daily streak, and unlock +25 XP toward your next engineering tier.

⚡

Connected ChemProCal Tool

Run numerical simulations with real physical property packages.
Psychrometric & HVAC Analyzer

Rigorous CoolProp inverse solver and HVAC process analysis for cooling, heating, and dehumidification loads.

Verified Equations Engineering Tolerances
Launch Live Tool ⚡