PID Control Modes (Proportional, Integral, Derivative Action)
Covers Proportional-Integral-Derivative (PID) control modes, analyzing mathematical controller algorithms, proportional band, steady-state offset elimination, derivative lead action, and direct versus reverse action.
1. Theoretical Foundations & Engineering Mechanics
Industrial Feedback Control Architecture
In a feedback loop, the controller compares the measured process variable $y(t)$ against the desired setpoint $y_{sp}(t)$ to compute the error signal:
$$e(t) = y_{sp}(t) - y(t)$$
The standard ideal continuous PID controller algorithm calculates the manipulated variable output $u(t)$ as:
$$u(t) = \bar{u} + K_c \left[ e(t) + \frac{1}{\tau_I} \int_0^t e(t') dt' + \tau_D \frac{de(t)}{dt} \right]$$
Where $\bar{u}$ is the nominal bias (manual reset) output, $K_c$ is controller gain, $\tau_I$ is integral (reset) time, and $\tau_D$ is derivative (rate) time.
The Laplace transform of the controller output (in deviation variables) is:
$$G_c(s) = \frac{U(s)}{E(s)} = K_c \left( 1 + \frac{1}{\tau_I s} + \tau_D s \right) = K_c + \frac{K_I}{s} + K_D s$$
Individual Control Mode Roles
- Proportional Mode ($P$): Produces a control action directly proportional to current error. Characterized either by gain $K_c$ or Proportional Band ($PB$):
$$PB = \frac{100\%}{K_c}$$
P-only control always leaves a persistent steady-state offset following load disturbances because a non-zero error is required to sustain valve displacement away from bias $\bar{u}$. - Integral Mode ($I$): Accumulates past error over time. Continues driving the control valve until error is driven strictly to zero:
$$\lim_{t \to \infty} e(t) = 0$$
However, integral action introduces a pole at the origin ($1/s$), adding $-90^\circ$ of phase lag and reducing closed-loop stability margins. - Derivative Mode ($D$): Anticipates future error trajectory based on current rate of change $de/dt$. Provides phase lead ($+90^\circ$), boosting stability and enabling higher controller gains, but drastically amplifies high-frequency measurement noise.
Direct vs Reverse Controller Action
- Direct Acting ($K_c < 0$ or +Action): Controller output increases when measurement increases ($PV \uparrow \implies OUT \uparrow$). Example: Level control where valve drains bottom liquid.
- Reverse Acting ($K_c > 0$ or -Action): Controller output decreases when measurement increases ($PV \uparrow \implies OUT \downarrow$). Example: Heat exchanger steam valve (temperature rises $\implies$ throttle steam valve shut).
2. Governing Equations & Mathematical Formulation
$$e(t) = y_{sp}(t) - y(t)$$
$$u(t) = \bar{u} + K_c \left[ e(t) + \frac{1}{\tau_I} \int_0^t e(t') dt' + \tau_D \frac{de}{dt} \right]$$
$$G_c(s) = K_c \left( 1 + \frac{1}{\tau_I s} + \tau_D s \right)$$
$$PB = \frac{100\%}{|K_c|}$$
$$\text{Offset} = e(\infty) = \frac{\Delta y_{sp}}{1 + K_{ol}} + \frac{K_d \Delta d}{1 + K_{ol}}$$
• The feedback error signal is computed instantaneously without transmission lag.
• Actuator response is linear and unsaturated between 0% and 100% stroke.
• Derivative mode incorporates a first-order noise filter: $G_D(s) = \frac{\tau_D s}{\alpha \tau_D s + 1}$ with $\alpha \approx 0.05 - 0.1$.
• The process can be adequately represented by linear transfer functions around the operating point.
• Confusing reset time $\tau_I$ (minutes/repeat) with reset rate $1/\tau_I$ (repeats/minute) on industrial DCS configuration screens.
• Specifying incorrect controller action (direct instead of reverse), causing positive feedback and driving valves immediately to full-open or full-closed saturation.
• Using derivative action on noisy signals (such as liquid level or orifice flow meters) without adequate pre-filtering.
• Attempting to eliminate steady-state offset with P-only control by cranking up $K_c$ to infinity, inducing sustained closed-loop oscillations.
3. Applied Engineering Worked Example
Standard industrial operating and sizing conditions.
Problem Statement:
A chemical reactor temperature process has transfer function $G_p(s) = \frac{2.5}{4.0 s + 1}\text{ }[^\circ\text{C}/\%]$ and disturbance transfer function $G_d(s) = \frac{1.0}{4.0 s + 1}\text{ }[^\circ\text{C}/(\text{kg/min})]$. The sensor and control valve have unity steady-state gains ($K_m = 1, K_v = 1$).
- For a proportional-only controller with $K_c = 3.0\text{ \%/}^\circ\text{C}$, calculate the closed-loop steady-state offset resulting from a disturbance load step $\Delta d = +5.0\text{ kg/min}$.
- Calculate the corresponding Proportional Band ($PB$).
- Show that adding integral action ($G_c(s) = K_c (1 + 1/(\tau_I s))$) reduces the steady-state offset to exactly zero.
Step-by-Step Analytical Solution:
-
P-only closed-loop offset:
Closed-loop load transfer function:
$$\frac{Y(s)}{D(s)} = \frac{G_d(s)}{1 + G_c(s) G_p(s)} = \frac{\frac{1.0}{4.0 s + 1}}{1 + 3.0 \frac{2.5}{4.0 s + 1}} = \frac{1.0}{(4.0 s + 1) + 7.5} = \frac{1.0}{4.0 s + 8.5}$$
For a step disturbance $D(s) = \frac{5.0}{s}$:
Applying the Final Value Theorem:
$$y'(\infty) = \lim_{s \to 0} [s Y(s)] = \lim_{s \to 0} \left[ s \cdot \frac{1.0}{4.0 s + 8.5} \cdot \frac{5.0}{s} \right] = \frac{5.0}{8.5} = \mathbf{0.588^\circ\text{C}}$$
Since $y_{sp} = 0$, the steady-state offset is:
$$\text{Offset} = y_{sp} - y'(\infty) = 0 - 0.588 = \mathbf{-0.588^\circ\text{C}}$$ -
Proportional Band ($PB$):
$$PB = \frac{100\%}{K_c} = \frac{100\%}{3.0} = \mathbf{33.33\%}$$ -
Elimination of offset via PI control:
With $G_c(s) = K_c \left( \frac{\tau_I s + 1}{\tau_I s} \right)$:
$$\frac{Y(s)}{D(s)} = \frac{G_d(s)}{1 + G_c(s) G_p(s)} = \frac{\frac{1.0}{4.0 s + 1}}{1 + K_c \frac{\tau_I s + 1}{\tau_I s} \frac{2.5}{4.0 s + 1}} = \frac{\tau_I s (4.0 s + 1)}{(4.0 s + 1)\tau_I s + 2.5 K_c (\tau_I s + 1)}$$
Applying Final Value Theorem for load step $D(s) = 5.0/s$:
$$y'(\infty) = \lim_{s \to 0} \left[ s \cdot \frac{\tau_I s}{\tau_I s (4.0 s + 1) + 2.5 K_c (\tau_I s + 1)} \cdot \frac{5.0}{s} \right] = \frac{0}{2.5 K_c} = \mathbf{0.000^\circ\text{C}}$$
Integral action completely drives the error and offset to zero.
Interactive Practice Drill: PID Control Modes (Proportional, Integral, Derivative Action)
Completed this lesson?
Record your study progress, build your daily streak, and unlock +25 XP toward your next engineering tier.
Connected ChemProCal Tool
Size control valves for incompressible fluids.