Direct Synthesis & Internal Model Control (IMC) Tuning Rules
Covers Direct Synthesis and Internal Model Control (IMC) controller design, analytical PI/PID parameter derivation, Skogestad SIMC tuning rules, and the trade-off between closed-loop speed and robustness.
1. Theoretical Foundations & Engineering Mechanics
Direct Synthesis Controller Design
Rather than relying on empirical formulas, Direct Synthesis designs the controller $G_c(s)$ analytically by specifying the desired closed-loop transfer function $(Y/Y_{sp})_d$:
$$\frac{Y(s)}{Y_{sp}(s)} = \frac{G_c(s) G_p(s)}{1 + G_c(s) G_p(s)} = \left(\frac{Y}{Y_{sp}}\right)_d$$
Solving algebraically for the required feedback controller:
$$G_c(s) = \frac{1}{G_p(s)} \frac{(Y/Y_{sp})_d}{1 - (Y/Y_{sp})_d}$$
For a process with dead time $\theta$, causality dictates that the closed loop must contain at least the same dead time. Specifying a first-order response with delay $\theta$ and tuning time constant $\tau_c$:
$$\left(\frac{Y}{Y_{sp}}\right)_d = \frac{e^{-\theta s}}{\tau_c s + 1}$$
Where $\tau_c$ is the single user-adjustable tuning parameter governing closed-loop speed versus robustness.
Skogestad's SIMC Tuning Rules
Sigurd Skogestad refined Direct Synthesis into the globally recognized Simple Control (SIMC) rules by utilizing a first-order Taylor approximation for dead time in the feedback path ($e^{-\theta s} \approx 1 - \theta s$):
For a standard First-Order Plus Dead Time (FOPDT) process $G_p(s) = \frac{K_p e^{-\theta s}}{\tau s + 1}$:
$$K_c = \frac{1}{K_p} \frac{\tau}{\tau_c + \theta}$$
$$\tau_I = \min\left[ \tau, 4(\tau_c + \theta) \right]$$
For an integrating process with delay $G_p(s) = \frac{K^* e^{-\theta s}}{s}$:
$$K_c = \frac{1}{K^*} \frac{1}{\tau_c + \theta}, \quad \tau_I = 4(\tau_c + \theta)$$
For a Second-Order Plus Dead Time process $G_p(s) = \frac{K_p e^{-\theta s}}{(\tau_1 s + 1)(\tau_2 s + 1)}$:
$$K_c = \frac{1}{K_p} \frac{\tau_1}{\tau_c + \theta}, \quad \tau_I = \min\left[ \tau_1, 4(\tau_c + \theta) \right], \quad \tau_D = \tau_2$$
Robustness Trade-off (The Choice of $\tau_c$)
- Fast / Aggressive: $\tau_c = \theta$ (provides $\approx 10\%$ overshoot, high gain margin $\text{GM} \approx 2.0$, phase margin $\text{PM} \approx 30^\circ$).
- Moderate / Standard Industrial: $\tau_c = \max(\tau, \theta)$ or $\tau_c = 2\theta$ (smooth setpoint tracking, zero overshoot, excellent robustness).
- Conservative / Noisy: $\tau_c = 3\theta$ to $5\theta$ (for high parameter uncertainty or severe measurement noise).
2. Governing Equations & Mathematical Formulation
$$G_c(s) = \frac{1}{G_p(s)} \frac{(Y/Y_{sp})_d}{1 - (Y/Y_{sp})_d}$$
$$\left(\frac{Y}{Y_{sp}}\right)_d = \frac{e^{-\theta s}}{\tau_c s + 1}$$
$$K_c = \frac{1}{K_p} \frac{\tau}{\tau_c + \theta}$$
$$\tau_I = \min\left[ \tau, 4(\tau_c + \theta) \right]$$
$$\tau_D = \tau_2 \quad \text{(for 2nd-order process)}$$
• The identified FOPDT process model matches physical plant dynamics with reasonable precision.
• Closed-loop response specification uses a first-order lag with pure delay.
• Actuator saturation limits are not violated during nominal setpoint transitions.
• Dead time is sufficiently small compared to total cycle time to allow Padé or Taylor series approximation.
• Selecting an unrealistically small closed-loop time constant ($\tau_c \to 0$), which demands infinite controller gain and drives valves into violent saturation.
• Omitting the integral time truncation $\min[\tau, 4(\tau_c + \theta)]$ for processes with very long time constants, which causes extreme settling times.
• Forgetting to invert the process gain $1/K_p$ when calculating $K_c$.
• Applying SIMC rules without matching controller algorithms (series vs parallel PID).
3. Applied Engineering Worked Example
Standard industrial operating and sizing conditions.
Problem Statement:
An amine regenerator reboiler steam loop is identified by plant step testing as a First-Order Plus Dead Time process:
$$G_p(s) = \frac{1.60 e^{-2.50 s}}{12.0 s + 1} \quad [^\circ\text{C}/\%]$$
Where time is in minutes.
- Using Skogestad's SIMC tuning method, design a PI controller for the standard robust setting $\tau_c = \theta = 2.50\text{ min}$.
- Calculate the resulting controller gain $K_c$ and integral reset time $\tau_I$.
- Design an alternative aggressive PI controller with $\tau_c = 0.5 \theta = 1.25\text{ min}$, and compare controller gains.
- Calculate the closed-loop time required to achieve $95\%$ setpoint tracking under the robust design.
Step-by-Step Analytical Solution:
-
Robust SIMC parameters ($\tau_c = \theta = 2.50\text{ min}$):
$$K_p = 1.60\text{ }[^\circ\text{C}/\%], \quad \tau = 12.0\text{ min}, \quad \theta = 2.50\text{ min}$$
$$\tau_c + \theta = 2.50 + 2.50 = 5.00\text{ min}$$
$$K_c = \frac{1}{K_p} \frac{\tau}{\tau_c + \theta} = \frac{1}{1.60} \frac{12.0}{5.00} = (0.625)(2.40) = \mathbf{1.50\text{ \%/}^\circ\text{C}}$$
$$\tau_I = \min[\tau, 4(\tau_c + \theta)] = \min[12.0, 4(5.00)] = \min[12.0, 20.0] = \mathbf{12.00\text{ min}}$$ -
Standard PI transfer function:
$$G_c(s) = 1.50 \left( 1 + \frac{1}{12.0 s} \right) = 1.50 + \frac{0.125}{s}$$ -
Aggressive design ($\tau_c = 1.25\text{ min}$):
$$\tau_c + \theta = 1.25 + 2.50 = 3.75\text{ min}$$
$$K_{c,agg} = \frac{1}{1.60} \frac{12.0}{3.75} = (0.625)(3.20) = \mathbf{2.00\text{ \%/}^\circ\text{C}}$$
$$\tau_{I,agg} = \min[12.0, 4(3.75)] = \min[12.0, 15.0] = \mathbf{12.00\text{ min}}$$
Notice gain increases by $33.3\%$ ($1.50 \to 2.00$). -
Settling time for robust design:
The desired closed loop is $y(t) = \Delta y_{sp} (1 - e^{-(t - \theta)/\tau_c}) S(t - \theta)$.
To reach $95\%$ ($1 - e^{-t'/\tau_c} = 0.95 \implies t' = 3\tau_c$):
$$t_{95} = \theta + 3\tau_c = 2.50 + 3(2.50) = 2.50 + 7.50 = \mathbf{10.00\text{ min}}$$