Log Mean Temperature Difference (LMTD) & Ft Correction Factor
Log Mean Temperature Difference (LMTD), Ft correction factor derivation, multi-pass configurations, and temperature cross mitigation.
1. Theoretical Foundations & Engineering Mechanics
Mean Temperature Difference & Multipass Thermal Efficiency
For a pure counter-current single-pass exchanger, the driving force is exactly the Log Mean Temperature Difference (LMTD). However, commercial shell and tube exchangers almost always feature multi-pass tube bundles (1-2, 1-4, 2-4 arrangements) where portions of the flow are co-current.
To account for the non-countercurrent driving force, the true mean temperature difference is corrected by the factor $F_t$:
$$\Delta T_m = F_t \cdot \Delta T_{lm,cf}$$
Key Parameters:
- Thermal Effectiveness ($P$): $P = \frac{t_2 - t_1}{T_1 - t_1}$ (ratio of actual heating of cold stream to maximum thermodynamic potential).
- Heat Capacity Ratio ($R$): $R = \frac{T_1 - T_2}{t_2 - t_1} = \frac{(\dot{m} C_p)_c}{(\dot{m} C_p)_h}$.
Temperature Cross:
When the cold fluid outlet temperature exceeds the hot fluid outlet temperature ($t_2 > T_2$), a "temperature cross" occurs. In a 1-shell pass exchanger, a temperature cross causes $F_t$ to drop precipitously below 0.80. Industry design practice prohibits operating with $F_t < 0.80$ because the design becomes hypersensitive to minor flow fluctuations, risking thermal stall.
2. Governing Equations & Mathematical Formulation
$$\Delta T_{lm} = \frac{(T_1 - t_2) - (T_2 - t_1)}{\ln\left( \frac{T_1 - t_2}{T_2 - t_1} \right)}$$
$$F_t = \frac{\sqrt{R^2 + 1} \ln\left( \frac{1 - P}{1 - P R} \right)}{(R - 1) \ln\left( \frac{2 - P(R + 1 - \sqrt{R^2 + 1})}{2 - P(R + 1 + \sqrt{R^2 + 1})} \right)} \quad (\text{1-2 Exchanger})$$
$$\text{For } R = 1: \quad F_t = \frac{\frac{\sqrt{2} P}{1 - P}}{\ln\left( \frac{2 - P(2 - \sqrt{2})}{2 - P(2 + \sqrt{2})} \right)}$$
• Overall heat transfer coefficient $U$ is constant throughout the entire exchanger.
• Specific heat capacities $C_p$ of both streams remain constant with temperature.
• No phase change occurs across the exchanger passes.
• Equal heat transfer area exists in each tube pass.
• Designing an exchanger with $F_t < 0.75$, leading to severe performance shortfall in the field.
• Attempting to solve a temperature cross with a single E-shell instead of splitting into two shells in series (F-shell or multiple 1-2 shells).
• Confusing shell-side temperatures ($T_1, T_2$) with tube-side temperatures ($t_1, t_2$) when evaluating $P$ and $R$.
3. Applied Engineering Worked Example
Hot Stream (Shell): Cools from $T_1 = 120^\circ\text{C}$ to $T_2 = 65^\circ\text{C}$
Cold Stream (Tubes): Heats from $t_1 = 40^\circ\text{C}$ to $t_2 = 75^\circ\text{C}$
Configuration: 1 Shell Pass, 2 Tube Passes (1-2 Exchanger)
-
Check for Temperature Cross:
$$t_2 = 75^\circ\text{C} > T_2 = 65^\circ\text{C} \implies \text{Temperature cross of } 10^\circ\text{C}!$$ -
Evaluate Dimensionless Parameters:
$$P = \frac{75 - 40}{120 - 40} = \frac{35}{80} = 0.4375$$
$$R = \frac{120 - 65}{75 - 40} = \frac{55}{35} = 1.5714$$
$$P \cdot R = 0.4375 \times 1.5714 = 0.6875 < 1.0$$ -
Calculate Counter-Current LMTD:
$$\Delta T_1 = 120 - 75 = 45^\circ\text{C}, \quad \Delta T_2 = 65 - 40 = 25^\circ\text{C}$$
$$\Delta T_{lm} = \frac{45 - 25}{\ln(45/25)} = \frac{20}{0.5878} = 34.03^\circ\text{C}$$ -
Calculate $F_t$ Factor:
$$\sqrt{R^2 + 1} = \sqrt{1.5714^2 + 1} = \sqrt{3.469} = 1.8626$$
Evaluating the 1-2 formulation gives $F_t \approx 0.61$. -
Engineering Conclusion:
Since $F_t = 0.61 < 0.80$, a single 1-2 shell cannot be used. We must specify two shells in series (2-4 exchanger) where each shell handles half the temperature change, restoring $F_t$ to $\approx 0.94$.