Process Identification: Open-Loop Step Testing & FOPDT Model Fitting
Covers open-loop step testing and First-Order Plus Dead Time (FOPDT) system identification, detailing tangent-and-intercept construction, two-point methods (Sundaresan-Krishnaswamy, Smith), and process gain estimation.
1. Theoretical Foundations & Engineering Mechanics
Industrial Process Identification
The overwhelming majority of chemical processes can be adequately approximated near an operating point by a First-Order Plus Dead Time (FOPDT) dynamic model:
$$G_p(s) = \frac{K_p e^{-\theta s}}{\tau s + 1}$$
Determining the three fundamental model parameters—static process gain ($K_p$), effective time constant ($\tau$), and apparent dead time ($\theta$)—is accomplished by conducting an open-loop plant bump (step) test.
Open-Loop Step Test Procedure
- Place the controller in Manual mode and allow the process variable $y$ to reach a steady baseline.
- Step the controller output to the valve by magnitude $\Delta u$ (typically $3\%$ to $10\%$ of full stroke).
- Record the resulting S-shaped process reaction curve until a new steady state is reached ($y_\infty$).
The process gain is calculated directly from the total steady-state change:
$$K_p = \frac{\Delta y_\infty}{\Delta u} = \frac{y_\infty - y_0}{u_\infty - u_0}$$
Method 1: Tangent-and-Intercept (Ziegler-Nichols)
- Draw a straight line tangent to the inflection point (maximum slope) of the S-shaped response curve.
- The time where this tangent intersects the initial baseline $y_0$ defines apparent dead time $\theta$.
- The time where the tangent intersects the final steady state $y_\infty$ equals $\theta + \tau$.
- Limitation: Highly sensitive to measurement noise at the inflection point.
Method 2: Two-Point Method (Smith / Sundaresan & Krishnaswamy)
To eliminate subjective tangent drawing, modern automated DCS packages sample two points on the normalized response curve $y_N(t) = \frac{y(t) - y_0}{y_\infty - y_0}$:
-
Sundaresan-Krishnaswamy Method:
- Record $t_{35.3\%}$ (time to reach $35.3\%$ of total change).
- Record $t_{85.3\%}$ (time to reach $85.3\%$ of total change).
$$\tau = 0.67 (t_{85.3\%} - t_{35.3\%})$$
$$\theta = 1.30 t_{35.3\%} - 0.29 t_{85.3\%}$$ -
Smith's Two-Point Method:
- Record $t_{28.3\%}$ (time to reach $28.3\%$ where $t = \theta + \tau/3$).
- Record $t_{63.2\%}$ (time to reach $63.2\%$ where $t = \theta + \tau$).
$$\tau = 1.50 (t_{63.2\%} - t_{28.3\%})$$
$$\theta = t_{63.2\%} - \tau$$
2. Governing Equations & Mathematical Formulation
$$K_p = \frac{\Delta y_\infty}{\Delta u}$$
$$G_p(s) = \frac{K_p e^{-\theta s}}{\tau s + 1}$$
$$\tau_{Smith} = 1.50 (t_{63.2\%} - t_{28.3\%})$$
$$\theta_{Smith} = t_{63.2\%} - \tau$$
$$\tau_{SK} = 0.67 (t_{85.3\%} - t_{35.3\%}), \quad \theta_{SK} = 1.30 t_{35.3\%} - 0.29 t_{85.3\%}$$
• The system starts at an exact quiescent steady state prior to the bump test.
• No external unmeasured load disturbances enter during the recording period.
• Actuator moves monotonically without stiction-induced stick-slip jumps.
• Signal-to-noise ratio is sufficiently high to accurately identify the fractional percentage points.
• Aborting the step test too early before true steady state is achieved, which severely underestimates both gain $K_p$ and time constant $\tau$.
• Introducing too large a step $\Delta u$ that drives the process into non-linear saturation or trips safety alarms.
• Introducing too small a step where process noise obscures the true reaction curve.
• Drawing the tangent line at the wrong slope due to high-frequency sensor ripple.
3. Applied Engineering Worked Example
Standard industrial operating and sizing conditions.
Problem Statement:
An engineer conducts an open-loop step test on a natural gas sweetening contactor column differential pressure loop. At initial steady state, the gas bypass control valve is at $u_0 = 35.0\%$ and the column DP is steady at $\Delta P_0 = 4.20\text{ kPa}$.
At $t = 0$, the valve is stepped to $u = 42.0\%$ ($\Delta u = +7.0\%$). The column differential pressure climbs smoothly to a final steady state $\Delta P_\infty = 7.70\text{ kPa}$.
The following time milestones are extracted from the DCS trend:
- Time to reach $28.3\%$ change ($5.19\text{ kPa}$): $t_{28.3\%} = 3.60\text{ min}$
- Time to reach $63.2\%$ change ($6.41\text{ kPa}$): $t_{63.2\%} = 8.40\text{ min}$
- Calculate the static process gain $K_p$.
- Using Smith's two-point method, determine the effective time constant $\tau$ and apparent dead time $\theta$.
- Formulate the identified FOPDT transfer function $G_p(s)$.
- Calculate the fractional dead time ratio $r = \theta / \tau$ and classify the difficulty of controlling this loop.
Step-by-Step Analytical Solution:
-
Static process gain $K_p$:
$$\Delta y_\infty = 7.70 - 4.20 = 3.50\text{ kPa}$$
$$\Delta u = 42.0 - 35.0 = 7.0\%$$
$$K_p = \frac{\Delta y_\infty}{\Delta u} = \frac{3.50\text{ kPa}}{7.0\%} = \mathbf{0.500\text{ kPa/\%}}$$ -
Smith's two-point parameter fitting:
$$\tau = 1.50 (t_{63.2\%} - t_{28.3\%}) = 1.50 (8.40 - 3.60) = 1.50 (4.80) = \mathbf{7.20\text{ min}}$$
$$\theta = t_{63.2\%} - \tau = 8.40 - 7.20 = \mathbf{1.20\text{ min}}$$ -
Identified transfer function:
$$G_p(s) = \mathbf{\frac{0.500 e^{-1.20 s}}{7.20 s + 1}}$$ -
Fractional dead time ratio:
$$r = \frac{\theta}{\tau} = \frac{1.20\text{ min}}{7.20\text{ min}} = \mathbf{0.1667}$$
Since $r < 0.25$, the process is lag-dominant (easily controllable with a standard PI controller).
Interactive Practice Drill: Process Identification: Open-Loop Step Testing & FOPDT Model Fitting
Completed this lesson?
Record your study progress, build your daily streak, and unlock +25 XP toward your next engineering tier.