API 521 External Fire Case (Wetted Surface & F-Factor)
API Standard 521 pool fire heat absorption equations for liquid-wetted vessels, prompt firefighting factors, wetted area calculations, and latent heat boiling relief loads.
1. Theoretical Foundations & Engineering Mechanics
API Standard 521 Pool Fire Relief for Wetted Vessels
When a vessel containing liquid is enveloped in an external hydrocarbon pool fire, intense thermal radiation ($80$ to $100\text{ kW/m}^2$) boils the inventory. The generated vapor must be vented through a relief valve to prevent vessel rupture.
1. Heat Absorption Equations (API 521)
The total heat absorption $Q$ into the wetted internal surface is calculated by empirical formulas:
- With Prompt Firefighting & Drainage:
$$Q = 43,200 \cdot F \cdot A_{w}^{0.82} \quad [Q: \text{W}, A_w: \text{m}^2]$$
$$Q = 21,000 \cdot F \cdot A_{w}^{0.82} \quad [Q: \text{Btu/h}, A_w: \text{ft}^2]$$
- Without Prompt Firefighting or Poor Drainage:
$$Q = 70,900 \cdot F \cdot A_{w}^{0.82} \quad [Q: \text{W}, A_w: \text{m}^2]$$
$$Q = 34,500 \cdot F \cdot A_{w}^{0.82} \quad [Q: \text{Btu/h}, A_w: \text{ft}^2]$$
2. Environmental Factor ($F$)
- Bare metal vessel: $F = 1.0$
- Insulated vessel (fireproof cellular glass/calcium silicate with stainless steel jacketing): $F = 0.075$ to $0.30$ depending on insulation conductance $k/\delta$.
- Water spray / deluge systems: API 521 does NOT credit water spray ($F = 1.0$) because piping is vulnerable to blast damage.
3. Wetted Surface Area ($A_w$) Determination
Fire height is limited to $7.6\text{ m}$ ($25\text{ ft}$) above the source of fire (grade or solid deck):
- Horizontal Vessels: Wetted surface up to maximum liquid operating level or $7.6\text{ m}$ elevation, whichever is lower.
- Vertical Vessels: Wetted sidewall up to maximum normal liquid level, but not exceeding $7.6\text{ m}$ elevation plus bottom head area.
- Spherical Vessels: Wetted surface up to horizontal equator or $7.6\text{ m}$ elevation.
4. Relieving Load Calculation
The required mass relief rate $W$ is the heat input divided by the fluid’s latent heat of vaporization $\Delta H_{vap}$ at relieving conditions:
$$W = \frac{Q}{\Delta H_{vap}}$$
2. Governing Equations & Mathematical Formulation
$$Q = 43,200 \cdot F \cdot A_w^{0.82} \quad [\text{SI: Watts, } A_w \text{ in m}^2]$$
$$W = \frac{Q}{\Delta H_{vap}} \times 3600 \quad [W: \text{kg/h}, Q: \text{W}, \Delta H_{vap}: \text{J/kg}]$$
$$P_{rel} = 1.21 \times P_{set} + P_{atm} \quad \text{[Fire Case allows 21% Overpressure per ASME]}$$
• Fire pool is at grade; thermal radiation does not extend higher than $7.6\text{ m}$ ($25\text{ ft}$) above fuel surface.
• ASME Section VIII allows 21% accumulation for fire contingency (vs 10% for operational cases).
• Liquid is at its boiling point at relieving pressure.
• Using ambient temperature latent heat $\Delta H_{vap}$ instead of the much lower latent heat near critical pressure, leading to dangerous undersizing.
• Taking credit for insulation ($F < 1.0$) when aluminum jacketing is used (aluminum melts at $660^\circ\text{C}$ in a $1000^\circ\text{C}$ hydrocarbon fire; stainless steel banding and jacketing are required).
• Calculating wetted area for vertical columns up to the top tangent instead of capping at the $7.6\text{ m}$ flame limit.
3. Applied Engineering Worked Example
Equipment: Horizontal Propane Surge Drum (Bare carbon steel, $F = 1.0$)
Dimensions: Diameter $D = 2.4\text{ m}$, Tan-to-Tan Length $L = 8.0\text{ m}$, 2:1 Semi-elliptical heads
Liquid Level: Normal liquid level at centerline ($50\%$ full $\implies A_w = \text{half shell} + \text{half heads}$)
Operating Elevation: Centerline at $3.5\text{ m}$ above grade (fully below $7.6\text{ m}$ flame zone)
Fluid: Propane at 21% overpressure ($P_{set} = 15.0\text{ barg} \implies P_1 = 19.16\text{ barg} = 20.17\text{ bara}$)
Properties at Relieving Conditions: Latent heat $\Delta H_{vap} = 285\text{ kJ/kg} = 285,000\text{ J/kg}$
-
Calculate Total Wetted Surface Area ($A_w$):
- Cylinder Area: $A_{cyl} = \pi D L = \pi \times 2.4 \times 8.0 = 60.32\text{ m}^2$
- Head Area (two 2:1 heads): $2 \times (1.084 D^2) = 2 \times (1.084 \times 5.76) = 12.49\text{ m}^2$
- Total Wetted Area at 50% level: $A_w = 0.5 \times (60.32 + 12.49) = 36.41\text{ m}^2$ -
Compute Heat Absorption ($Q$):
Assuming adequate drainage and prompt firefighting:
$$Q = 43,200 \times 1.0 \times (36.41)^{0.82} = 43,200 \times 19.206 = 829,700\text{ W} = 829.7\text{ kW}$$ -
Calculate Required Relieving Vapor Rate:
$$W = \frac{Q}{\Delta H_{vap}} = \frac{829,700\text{ J/s}}{285,000\text{ J/kg}} = 2.911\text{ kg/s} = 10,480\text{ kg/h}$$ -
Conclusion:
The PSV must be sized to vent $10,480\text{ kg/h}$ of propane vapor at $20.17\text{ bara}$.